에너지/열교해석관련 질문

수성연질폼, 경질폼 캐나다 제품 - 성능표 좀 해석해주세요

G catfishkr 2 1,567 2018.09.23 07:09
PART 2 - PRODUCTS
2.1 MANUFACTURERS
A. Polyurethane Spray Foam Insulation: Icynene ClassicTM by Icynene Inc.
B. Intumescent paint:
1. DC-315 by International Fireproof Technology Inc.
2. Fireshell F10E by TPR2
3. No-Burn Plus ThB by No-Burn
2.2 MATERIALS
A. General: Provide insulating materials that comply with requirements and with
referenced standards.
B. Icynene ClassicTM (LD-C-50) Spray Foam Insulation: Low-density, water-blown,
conforming to the following:
1. Thermal Resistance (R-Value/inch @75 deg F): ASTM C 518; 3.7 hr/sq
ft/degree F/BTU
2. Air Permeance (for 3 inches of material): ASTM E 2178; < 0.014 L/s.m2
@ 75 Pa
3. Water Vapor Transmission (for 5.5 inches of material): ASTM E 96; 11
perms [627 ng /(Pa.s.m2
)]
4. Flame Spread and Smoke Developed Rating: ASTM E 84
a. Flame Spread: Less than 20
b. Smoke Development: Less than 400
5. Bacterial and Fungal Growth and Food Value: ASTM C 1338: no growth
C. Product Description:
1. ICC/ES Evaluation Report No. ESR 1826
2. Collaborative for High-Performance Schools (CHPS) “Low-emitting
material” per CA 01350 Criteria
D. Intumescent Paint
1. DC-315 Thermal Barrier Coating: 14 wet mils
2. Fireshell F10E Thermal Barrier Coating: 21 wet mils
3. No-Burn Plus ThB Thermal Barrier Coating: 18 wet mils

PART2 MATERIALS
General:  Provide insulating materials that comply with requirements and with referenced standards.
Icynene ProSeal HFO™ Spray Foam Insulation:  Medium-density, closed-cell, conforming to the following material performance:
Thermal Resistance (for 1 inch of material) (R-Value/inch @75 deg F):  ASTM C 518; 6.2 hr.sq ft.degree F/BTU
Thermal Resistance (for 3.5 inch of material) (R-Value/inch @75 deg F):  ASTM C 518; 24 hr.sq ft.degree F/BTU
Air Permeance (for 1 inch of material):  ASTM E 2178; less than 0.02 L/s*m2 @75 Pa
Water Vapor Transmission (for 1.4 inches of material):  ASTM E 96; 0.95 perm
Resistance to Fungal Growth: ASTM C 1338: no growth
Flame Spread and Smoke Developed Rating:  ASTM E 84
Flame Spread: 15
Smoke Development: 350
HFO Blowing Agent with Global Warming Potential: 1
Greenguard Gold Certified
DC-315: Intumescent paint
Thermal Barrier Coating: 14 wet mils
No-Burn Plus ThB Thermal Barrier Coating: 18 wet mils

Comments

M 관리자 2018.09.27 09:58
모든 줄을 다 말씀드리기 보다는 아래 글의 설명과 부합하는 내용이라, 링크의 글을 읽어 보시면 되실 것 같습니다.
http://www.phiko.kr/bbs/board.php?bo_table=z3_01&wr_id=1251
2 TBBlock 2018.09.27 16:13
단열재에 관련한 내용이 많기는 하지만 결국 가장 중요한 것은 열전도율과 난연성능입니다.
물론 습기과 관련된 내용도 중요합니다만 논외로 하겠습니다.

문의하신 내용은 연질폼과 경질폼(closed-cell)을 비교하는 것입니다.

연질폼은 open cell 이라 열전도율이 상대적으로 높습니다.
글에서는 3.7 hr/sqft/degree F/BTU 이라고 합니다.
단위가 열저항입니다.
경질폼은 6.2 hr.sq ft.degree F/BTU 로 대략 167% 열저항이 높네요..
단위가 열저항이니 숫자가 높을 수록 단열성능은 좋은 것입니다.

난연성은 ASTM E84 시험 방법으로 비교했는데 경질폼이 근소하게 앞서는 것으로 나왔습니다.
난연성 시험결과를 유심히 보실 필요가 있습니다.
ASTM E84 시험은 가로 폭 0.5 m x 12 m 정도로 큰 시험편으로 시험하는 방법입니다.
시험결과가 연질과 경질폼 사이에 유의미한 차이가 보이지 않습니다.

여기서.. 국내 수성연질폼이 준불연이라고 광고하는 제품들이 종종있습니다만..
그것은 제품 크기가 0.1 x 0.1 x 0.05m 크기로 시험하는 결과입니다.
난연성능이 준불연이라고 불에 타지 않는 것이 아니라
시편 크기가 커지면.. 일단 연기가 엄청나게 발생합니다.

화재가 발생하면 불 자체로 인한 피해보다 연기로 인한 피해가 더 큰 것을 고려해 볼 때
연질이나 경질이나 큰 차이가 없는 것으로 보입니다..

물론 문의하신 제품끼리 비교입니다..